Propex and Westy tank - now fixed.

Post by Wychall »

I have a Propex 2000 heater which has been working fine from a propane cylinder. I have now fitted a Westy underslung tank and plumbed it through with 8mm copper pipe. But now the Propex won't fire. I just get the two flashes to signify a gas problem.

I have checked that gas is getting to the heater (by loosening the union and listening to the hiss, but don't tell anyone). So what next? Will a 37 mbar heater run on a 50 mbar supply? Could the hiss fail to indicate insufficient flow? How can I check it?

Unfortunately I do not have a spare union to be able to revert to the cylinder to check that way. Perhaps I need to order one.
Last edited by Wychall on 20 Nov 2016, 14:37, edited 1 time in total.
.
South African 1991 2.5i Microbus - now sadly rehomed to pay for a Melco EMT16X Embroidery Machine.

User avatar
Oldiebut goodie
Registered user
Posts: 7295
Joined: 18 Apr 2008, 01:19
80-90 Mem No: 11135
Location: Eastern Angle

Re: Propex and Westy tank

Post by Oldiebut goodie »

Obvious answer is that your gas pressure is way too high! I should think that you need to fit the correct regulator to suit the Propex. (and other UK spec appliances)
1.6D 2019 VW T-Cross
200hp VW T6
1̶Y̶ ̶1̶9̶8̶7̶ ̶H̶i̶-̶t̶o̶p̶ ̶C̶a̶r̶a̶v̶e̶l̶l̶e̶
5̶0̶8̶d̶ ̶M̶e̶r̶c̶

User avatar
Wychall
Trader
Posts: 879
Joined: 17 Jun 2011, 22:48
80-90 Mem No: 9841
Location: South Birmingham
Contact:

Re: Propex and Westy tank

Post by Wychall »

That's what I thought, but I am sure I read on this exalted forum that the Propex would happily run on the Westy pressure. Time to search all the old posts I think.
.
South African 1991 2.5i Microbus - now sadly rehomed to pay for a Melco EMT16X Embroidery Machine.

User avatar
Oldiebut goodie
Registered user
Posts: 7295
Joined: 18 Apr 2008, 01:19
80-90 Mem No: 11135
Location: Eastern Angle

Re: Propex and Westy tank

Post by Oldiebut goodie »

Apparently Propex do make a 50mbar version but standard is 28 or 30 mbar according to their literature for the 1800.
1.6D 2019 VW T-Cross
200hp VW T6
1̶Y̶ ̶1̶9̶8̶7̶ ̶H̶i̶-̶t̶o̶p̶ ̶C̶a̶r̶a̶v̶e̶l̶l̶e̶
5̶0̶8̶d̶ ̶M̶e̶r̶c̶

User avatar
Wychall
Trader
Posts: 879
Joined: 17 Jun 2011, 22:48
80-90 Mem No: 9841
Location: South Birmingham
Contact:

Re: Propex and Westy tank

Post by Wychall »

I was sure that I had seen something. Evidently Mr Titus has his working ok. Hopefully he will be along to confirm.
http://forum.club8090.co.uk/viewtopic.p ... 5#p8143883" onclick="window.open(this.href);return false;
.
South African 1991 2.5i Microbus - now sadly rehomed to pay for a Melco EMT16X Embroidery Machine.

User avatar
Oldiebut goodie
Registered user
Posts: 7295
Joined: 18 Apr 2008, 01:19
80-90 Mem No: 11135
Location: Eastern Angle

Re: Propex and Westy tank

Post by Oldiebut goodie »

Hmmm.....Maybe Titus's was a 50 mbar one to start with? He may have got his locally in Germany. I would expect the flame to be prone to blowing out at the higher pressure. Might be better to get paulandchez to confirm whether his is OK on the high pressure tank or that he had to use another regulator.
1.6D 2019 VW T-Cross
200hp VW T6
1̶Y̶ ̶1̶9̶8̶7̶ ̶H̶i̶-̶t̶o̶p̶ ̶C̶a̶r̶a̶v̶e̶l̶l̶e̶
5̶0̶8̶d̶ ̶M̶e̶r̶c̶

User avatar
Titus A Duxass
Registered user
Posts: 5778
Joined: 24 Nov 2007, 08:22
80-90 Mem No: 4475
Location: Cologne

Re: Propex and Westy tank

Post by Titus A Duxass »

Mine Is a UK sourced Propex.
I have it plumbed in to the westy tank and it runs fine.
Steve at gasure told me that they run okay with 50mb.
VW T3 GTi Camper 2,0l

User avatar
Wychall
Trader
Posts: 879
Joined: 17 Jun 2011, 22:48
80-90 Mem No: 9841
Location: South Birmingham
Contact:

Re: Propex and Westy tank

Post by Wychall »

Titus A Duxass wrote:Mine Is a UK sourced Propex.
I have it plumbed in to the westy tank and it runs fine.
Steve at gasure told me that they run okay with 50mb.

Thanks for the confirmation. I now need to get another coupler so that I can switch back to a cylinder to try and isolate my problem.
.
South African 1991 2.5i Microbus - now sadly rehomed to pay for a Melco EMT16X Embroidery Machine.

User avatar
Wychall
Trader
Posts: 879
Joined: 17 Jun 2011, 22:48
80-90 Mem No: 9841
Location: South Birmingham
Contact:

Re: Propex and Westy tank

Post by Wychall »

So, I have cut into my new copper line so that I can connect with a rubber hose to a propane cylinder. The Propex then fired up immediately. My problem is therefore with either pressure or flow rate through the Westy regulator. As Titus confirms that the Propex should be ok at 50 mbar I now need to check the flow rate. How the heck do I do that? I'm thinking perhaps a roofing torch to make sure I can get a substantial flame. What do you think?

Also, has anyone used a Tinley Tech regulator to replace the Westy one? Will it fit?
.
South African 1991 2.5i Microbus - now sadly rehomed to pay for a Melco EMT16X Embroidery Machine.

User avatar
Oldiebut goodie
Registered user
Posts: 7295
Joined: 18 Apr 2008, 01:19
80-90 Mem No: 11135
Location: Eastern Angle

Re: Propex and Westy tank

Post by Oldiebut goodie »

Why not just put the correct regulator in line? It would save a lot of faffing about like you are proposing. £20 ish for a bulkhead one like you need.
1.6D 2019 VW T-Cross
200hp VW T6
1̶Y̶ ̶1̶9̶8̶7̶ ̶H̶i̶-̶t̶o̶p̶ ̶C̶a̶r̶a̶v̶e̶l̶l̶e̶
5̶0̶8̶d̶ ̶M̶e̶r̶c̶

User avatar
captain Byrne
Registered user
Posts: 1004
Joined: 19 Mar 2009, 10:01
80-90 Mem No: 7107
Location: Glasgow
Contact:

Re: Propex and Westy tank

Post by captain Byrne »

They're designed to run at 30mb. Some may work ok at 50 but that's nearly twice the pressure. If it does run it'll be inefficient, you'll probably get flame 'lift off' and it won't be good for the combustion chamber & will probably shorten the heater's life. You need a 30mb governor (regulator). http://www.autogasshop.co.uk/truma-in-l ... -604-p.asp" onclick="window.open(this.href);return false;
Pretty simple to fit in-line but I suppose you should get a Gas Safe engineer to check it if you're not too confident with gas.
1983 LHD Westfalia poptop 1.9 DG petrol.

User avatar
Wychall
Trader
Posts: 879
Joined: 17 Jun 2011, 22:48
80-90 Mem No: 9841
Location: South Birmingham
Contact:

Re: Propex and Westy tank

Post by Wychall »

As I don't have a camper, space for a bulkhead or inline regulator is at a minimum. That is why I would prefer to find something that would fit within the Westy tank control box. The tinley reg is of the bulkhead type, utilising 8mm compression fittings each end. I was just hoping for confirmation that the threaded outlets are a match for the westy ones. I also have my doubts about the state of the existing regulator so would prefer to replace it rather than have a secondary step down.
Failing confirmation from anyone, I will order the tinley and keep my fingers crossed. It's only £20ish so not a bank breaker.
.
South African 1991 2.5i Microbus - now sadly rehomed to pay for a Melco EMT16X Embroidery Machine.

User avatar
Wychall
Trader
Posts: 879
Joined: 17 Jun 2011, 22:48
80-90 Mem No: 9841
Location: South Birmingham
Contact:

Re: Propex and Westy tank

Post by Wychall »

So due to the deafening silence from anyone that has replaced the Westy regulator I decided to break the ice myself. I ordered the 37 mbar regulator from Tinley and, on receipt of it realised that I had no chance of replacing the existing reg. It was at least twice the diameter!

Let's now follow the sage advice from Oldiebut goodie and fit it in line with the existing regulator.

All connected up, flick the switch, and bingo! It works!

I can now confirm that some propex heaters will NOT work at the Westy pressure of 50mbar and will need to be further reduced to 37 mbar.

I'm now ready for the severe winter that the weather forecasters are promising us. (I hope they are wrong though :rofl)
.
South African 1991 2.5i Microbus - now sadly rehomed to pay for a Melco EMT16X Embroidery Machine.

User avatar
captain Byrne
Registered user
Posts: 1004
Joined: 19 Mar 2009, 10:01
80-90 Mem No: 7107
Location: Glasgow
Contact:

Re: Propex and Westy tank - now fixed.

Post by captain Byrne »

Don't want to put a downer on things & I'm glad it's working but I can assure you it's not working correctly.
E.D.I.T. note to self .. read stuff properly before posting.
Last edited by captain Byrne on 20 Nov 2016, 22:45, edited 1 time in total.
1983 LHD Westfalia poptop 1.9 DG petrol.

User avatar
Oldiebut goodie
Registered user
Posts: 7295
Joined: 18 Apr 2008, 01:19
80-90 Mem No: 11135
Location: Eastern Angle

Re: Propex and Westy tank - now fixed.